RD35
Senior Member
- Location
- Bloomington, Indiana
I'm designing my first RV Park. The pedestals my customer wants are offered by more than one manufacturer and are very similar. They have a 2P50A, a 1P30A, and a 1P20A breaker with one receptacle each. Very common set-up. The breakers inside the pedestal are fed from a single phase 240V, 125A panel bus. The bus is fed by #1 copper tap conductors that are, in turn, fed by a set of lugs which also have double 6-350 barrels on each lug for the purpose of loop or daisy-chain feeders. From the data I have found I can both size and protect the feeders at an amperage up over 200A. The pedestal breaker bus is lug only (no MCB). So my question has to do with protecting that 125A bus. Is that bus considered protected so long as the total ampacity of the OCP on either bus bar does not exceed 125A? Is there a code section (tap rule maybe) that addresses this type of issue directly? (If so, I cannot seem to locate it)
Thanks
Thanks