I know this has been discussed before but I have a customer that needs a 50 amp RV receptacle attached to a detached building. Not sure if it needs GFCI protection from the panel or if I can use a RV panel that has GFCI protection and would that serve as a disconnect as well or would it need a disconnect beside of the RV panel? And if a disconnect is needed, could a breaker lock in the panel serve that purpose?
 
I know this has been discussed before but I have a customer that needs a 50 amp RV receptacle attached to a detached building. Not sure if it needs GFCI protection from the panel or if I can use a RV panel that has GFCI protection and would that serve as a disconnect as well or would it need a disconnect beside of the RV panel? And if a disconnect is needed, could a breaker lock in the panel serve that purpose?
Would something like this serve both purposes if needed?
 

Attachments

  • Screenshot_20250917_102247_Chrome.jpg
    Screenshot_20250917_102247_Chrome.jpg
    393.1 KB · Views: 5
My take on it is a RV feeder receptacles are exempt from GFCI the section is 551.71(F)(2) in the 2023 NEC.
The receptacle is the disconnect for the feeder.
 