milmat1
"It Can't Do That !"
- Location
- Siler City, NC USA
- Occupation
- Controls Engineer
As an OEM of industrial machinery we build our own panels and control systems in house. I am trying to get this shop up to speed on proper nameplate
installations on our cabinets. Which up until now has not been done at all..
Concerning the SCCR rating, I have been studying how to calculate these ratings and I have created a great deal of confusion...
Using the Idea of "weakest Link" , the lowest rated component in my cabinet can in many cases determine the SCCR. But that component (lets say its a overload or a motor starter or Dist block etc) is actually
behind several other protective components. Such as the main disconnect fuses / main breaker, MPCB etc or maybe a transformer. In other words it would never see the AFC from
the supplied power source. So why do the components downstream of the main OCPD control the SCCR rating?
I'm not wording this well I understand, But I'm trying to get my head around this SCCR rating and it's purpose. For example if a set of motor leads coming from the cabinet were to become faulted together or to ground etc. That fault current would be limited by several devices long before the main OCPD even seen a problem? So the supplied power and it's AFC would never come into play would it ?
Can anyone give me a kind of overview of the SCCR nameplate rating and how that rating interacts with the field installation of the machine / control panel...
installations on our cabinets. Which up until now has not been done at all..
Concerning the SCCR rating, I have been studying how to calculate these ratings and I have created a great deal of confusion...
Using the Idea of "weakest Link" , the lowest rated component in my cabinet can in many cases determine the SCCR. But that component (lets say its a overload or a motor starter or Dist block etc) is actually
behind several other protective components. Such as the main disconnect fuses / main breaker, MPCB etc or maybe a transformer. In other words it would never see the AFC from
the supplied power source. So why do the components downstream of the main OCPD control the SCCR rating?
I'm not wording this well I understand, But I'm trying to get my head around this SCCR rating and it's purpose. For example if a set of motor leads coming from the cabinet were to become faulted together or to ground etc. That fault current would be limited by several devices long before the main OCPD even seen a problem? So the supplied power and it's AFC would never come into play would it ?
Can anyone give me a kind of overview of the SCCR nameplate rating and how that rating interacts with the field installation of the machine / control panel...