Is there a code violation when running se cable through a cement basement wall into the panel?I see alot of homes done this way.If so what code ref.pertains to this.As always,thanks for the infor.
 
Re: s.e cable

If you mean running the SE cable inside the air voids of masonry block, then there is no problem.

If you mean running SE cable in a wall that will have poured concrete, then you are in violation.
 