G gerry Member Location New Jersey Jul 8, 2004 #1 Is there a code violation when running se cable through a cement basement wall into the panel?I see alot of homes done this way.If so what code ref.pertains to this.As always,thanks for the infor.
Is there a code violation when running se cable through a cement basement wall into the panel?I see alot of homes done this way.If so what code ref.pertains to this.As always,thanks for the infor.
J jcross Member Location Piney Flats, TN Jul 8, 2004 #2 Re: s.e cable I would think that 230.50 would address this. "Where subject to physical damage" would be the key statement.
Re: s.e cable I would think that 230.50 would address this. "Where subject to physical damage" would be the key statement.
B bphgravity Senior Member Location Florida Jul 8, 2004 #3 Re: s.e cable If you mean running the SE cable inside the air voids of masonry block, then there is no problem. If you mean running SE cable in a wall that will have poured concrete, then you are in violation.
Re: s.e cable If you mean running the SE cable inside the air voids of masonry block, then there is no problem. If you mean running SE cable in a wall that will have poured concrete, then you are in violation.