steve gottwald said:
What would the voltage drop be from supply(power pole) to breaker panel using 3/0 copper in a 450 foot run be.(200 amp main)

It would depend on the load.

Roger
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
It would also depend on whether you are talking about a single phase or three phase system.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
We should not be so hard on a new member.

Steve, your question does not give us enough information to help you get an answer. But we generally want to see you make some attempt to come up with an answer on your own. Let us know what you have tried, and what difficulties you have encountered, and we will know how best to help you.
 

electricalperson

Senior Member
Location
massachusetts
VD = 2KIL/CM

K = constant 12.9 copper 21.9 AL
I = amps
L = distance one way
CM = circular mils

3 phase

VD = 1.73KIL/CM

1.73 is the square root of 3

find wire size you need swap VD and CM

CM = 2kil/vd

you find VD by multiplying voltage by the % you want. 2.5 for example
 