SABC

Status
Not open for further replies.

nickelec

Senior Member
Location
US
Having a bit of a brain fart , can I feed the under cabinet lighting in my kitchen off the SABC or do I need to run it with the lighting circuit

Sent from my SM-G965U using Tapatalk
 
Not on the SABC.

210.52(B)(2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no
other outlets.

Exception No. 1: A receptacle installed solely for the electrical supply to and support of an electric clock in any of
the rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide power for supplemental equipment and lighting on gas-fired
ranges, ovens, or counter-mounted cooking units.
 
Thought so just finished running the feed from kitchen lighting!!

Sent from my SM-G965U using Tapatalk
 
You can't but I would do it anyway if I were adding them after the kitchen is finished. Is one LED strip light going to overload the circuit? :roll::roll::roll::roll::roll::roll::roll::roll:
 
No but when the inspector asks me to shut off the small appliance branch circuit and the under cabinet lights go off he might say something

Sent from my SM-G965U using Tapatalk
 