I was reading Mike's newsletter and this caught my eye. Does everyone agree with the interpretation?
NEC Questions and Answers – Based on the 2011 NEC
January 2012
By Mike Holt for EC&M Magazine
Here’s the follow up to Monday's newsletter. This includes all of the answers to the questions sent, so you can see how you did.
Q2. What are the Code requirements for small appliance branch circuits for dwelling units?
A2. Two or more 20A, 120V small-appliance receptacle branch circuits are required for the 15A or 20A receptacle outlets in a dwelling unit kitchen, dining room, breakfast room, pantry, or in similar dining areas as required by 210.52(B) [210.11(C)(1)].
Author’s Comments:
• See the definition of “Receptacle Outlet” in Article 100.
• A 15A, 125V receptacle is rated for 20A feed-through, so it can be used for this purpose [210.21(B)(3)].
• Lighting outlets or receptacles located in other areas of a dwelling unit must not be connected to the small-appliance branch circuit [210.52(B)(2)].
• The two 20A small-appliance branch circuits can be supplied by one 3-wire multiwire circuit or by two separate 120V circuits [210.4(A)].
• Each separate countertop must be supplied with two small-appliance circuits [210.52(B)(3)].