Bill Turax
Member
- Location
- MD
I have a job where the customer wanted cam-locks installed on the load side of a disconnect. the disconnect is 600v rated, NEMA 1 indoors. the load is 500 amps non continuous. service voltage is 480.
We installed parallel 1/0 SAE J1127 - Welding cable - rated for 600v and 350 amps at 50 foot.
He have welding cable installed from the load side of the disconnect to the cam-locks installed in the bottom of the disconnect. Inspector is saying that the welding cable is not permitted inside the disconnect.
My question is: What is the conde reference indicating that welding cable cannot be installed inside a disconnect.