megloff11x

Senior Member
I have an old building with three-phase 208 and its neutral coming in from the power company. The neutral is bonded to the building's metal structure, water pipes, etc.

We are adding disconnects to provide power for new machines. Some may require isolated grounds for noise reasons. Some won't.

NEC 250.24 describes adding a disconnect where the 3 phases and neutral wires (4 total) come in through the conduit to the box. The neutral bus is bonded to the box metal. The conduit is bonded to the service box and to the disconnect box. I refer to the 2002 handbook exhibits 250.10, 11, and 12, the last of which probably fits best.

There are cases in 250.96 where an isolated ground is needed, and it appears that in these cases, the neutral and ground wires are bonded together further "upstream" from the machine than in other cases. And they run a fifth "ground" wire.

Should I pull a separate, fifth green ground wire from the main service to each disconnect, or will using a four-wire system (3 phases & a neutral) and taking the fifth "ground" wire from the disconnect box's neutral bus suffice?

I am not so much concerned with noise issues as I am with different ground levels. I have seen computer signal wires throw sparks when plugged in, only to later find that the machine ground was tens of Volts different than the computer's ground (from the nearby 115V outlet), and the cable's shield was tied to chassis ground on both ends. This was in a particularly badly wired building.

I'm also concerned for the operator. For example in the 2002 NEC handbook exhibit 250.42, they show a subpanel system for isolated ground. How is that subpanel bonded to protect the user? Is it implied that the metal conduit pictured between it and the main service panel alone will do the trick? Some kinds of conduit do need an extra jumper, but they don't say what kind is used in their example. I see the subpanel box bonded to the ground bus inside the subpanel, but that ground bus is bonded to nothing else.

Bottom line, is it safe for machine and user to use four wires, five wires, or either?

Matt
 
Re: safe wiring for a new machine

What you're asking would be a code violation, if I understand the question. The only grounded to grounding conductor connection (bonding of neutral and ground) should be made in the main disconnect or main breaker panel. Everything else, disconnects, subpanels, etc should have their neutral and grounds isolated. You can't bond the neutral and ground in a machine disconnect.
 
Re: safe wiring for a new machine

Matt, I think you are asking for a complete grounding class in one question! When and where can service bonding be done, what is an effective equipment grounding conductor, what are the rules for an isolated(insulated equipment grounding conductor)ground, and how to eliminate noise on my grounding system. The answer is simple, hire an qualified electrical contractor to install the per NEC(as a minimum standard, especially Article 250) have it inspected by a certified electrical inspector, install a multi level TVSS protection system, and use your equipment with confidence.
Fred Bender
 
Re: safe wiring for a new machine

Matt, I hate jump on you also but these guys are absolutely correct. What is bothering me is that the profile says you are a consultant. Please, back off from this and get an electrical contractor involved to repair the electrical system before someone (even an IT guy) gets hurt or killed. :eek:
 
Re: safe wiring for a new machine

Originally posted by megloff11x:
Bottom line, is it safe for machine and user to use four wires, five wires, or either?

Matt
The answer is yes. :)

You have to be careful that you do not bond a neutral to ground at more than one place. That is both a code violation and a hazard.

Isolated grounds are not especially effective at reducing electrical noise, and are misnamed to boot. An isolated ground is simply a ground wire that is run from the service point in one length with the power wiring, rather than running it from point to point. It is not connected to the conduit system or anything else EXCEPT through its connection to the ground bar at the service point.
 
Re: safe wiring for a new machine

And of course, all NEC rules regarding Grounding and Bonding still apply, isolated ground or not.
 
Re: safe wiring for a new machine

Thanks all.

We have had a contractor putting in the new wiring the whole time. I was trying to avoid having to run the isolated ground wire from the main distribution. About all you get out of it is:

long wire = inductor = somewhat blocks high frequency noise.

Regarding tying ground and neutral in two places, I have seen a number of machines that take 5-wire (3 phases, neutral, and ground) but bond the ground bus to the neutral bus inside the machine. I'm trying to remember one I've seen that doesn't do this.

And regarding sparks and voltage differences between two "grounds," this was something I've seen in other facilities in the past, not the one at issue here. I mentioned it as something I was trying to avoid a repeat of.

I've had a lot of issues with instruments and machines vs. their power connection.

Matt
 
Re: safe wiring for a new machine

I would also question terminating both ends of a shield on a shielded communications cable - this creates another possible "ground" path or loop....... shields that we use (industrial/commercial) are only terminated at the closest point to the source end. The opposite end is pulled back over the cable and shrink tube is applied over the cable jacket to hold it in place.
 
Re: safe wiring for a new machine

The shield of a communications cable, such as 18-2, is only bonded at one end. Its not an equipment ground, its noise ground, so to speak. Bond it at the end it gets power from.
 
Re: safe wiring for a new machine

Originally posted by tom baker:
The shield of a communications cable, such as 18-2, is only bonded at one end. Its not an equipment ground, its noise ground, so to speak. Bond it at the end it gets power from.
"bond the ground bus to the neutral bus inside the machine." The neutral is a current carrying conductor, now you have neutral current on all the metal parts of a machine, in parallel with the neutral. This is a violation of Art 250.
 