Safety and hardwire question

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
If you have a commercial laundromat 2020 it appears if cord and plug connected the washer needs GFCI protection.

If hardwired it appears it is not necessary.

Why would hardwired be considered safe without GFCI protection?

Or am I incorrect
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Because GFCI protection is largely about accidental contact with plug blades.
Thank you Larry, being involved with industrial equipment I always had in my mind leakage current being a hazard that likely won’t trip a breaker.

I was not thinking of the attachment cord blades.

I always had the toaster example and touching the case in my head. Where the cord is not a factor
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
That's why most GFCI requirements are based on the location and purpose of the receptacle, and less so on the connected load.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Because GFCI protection is largely about accidental contact with plug blades.
I don't think so...The original reason was the idea that it is much more likely that the equipment grounding path will be compromised with cord and plug connected equipment as compared to hardwired equipment.
In fact, until recently the product listing standards for hard wired equipment did not even look a the issue of leakage current because the assumption is that the code required EGC eliminates the hazard from leakage current.
 