I am interested in any comments this community has on the following scenario:
The Contractor was unable to complete the installation. The existing 800AF/800AT main breaker will accommodate three 400 MCM conductors per phase but not the three 500 MCM conductors per phase as specified.
The Contractor was directed to use compression type pins to adapt the 500 MCM feeders to a size acceptable by the new triple lugs.
Before crimping the new compression pin to the conductor the Contractor assessed the final installation by inserting the pins in the lugs in the proper orientation. The diameter of the compression barrel forced the Contractor to orient the adapter such the pin embedment in the lug was not sufficient to tighten the hold-down screw. The lugs are physically too small to accommodate three 500 MCM conductors.
Therefore the Contractor replaced the original dual 500 MCM lugs on the existing main breaker and terminated only 2 of the 3 500 MCM per phase conductors. The third 500 MCM conductor was made safe at each end and secured to the back of each panel.
Since the main breaker is rated for 800 amps and dual 500 MCM conductors are rated for 760 amps (assuming 75-degree Celsius conductors were used) the interim installation is acceptable.
end
The Contractor was unable to complete the installation. The existing 800AF/800AT main breaker will accommodate three 400 MCM conductors per phase but not the three 500 MCM conductors per phase as specified.
The Contractor was directed to use compression type pins to adapt the 500 MCM feeders to a size acceptable by the new triple lugs.
Before crimping the new compression pin to the conductor the Contractor assessed the final installation by inserting the pins in the lugs in the proper orientation. The diameter of the compression barrel forced the Contractor to orient the adapter such the pin embedment in the lug was not sufficient to tighten the hold-down screw. The lugs are physically too small to accommodate three 500 MCM conductors.
Therefore the Contractor replaced the original dual 500 MCM lugs on the existing main breaker and terminated only 2 of the 3 500 MCM per phase conductors. The third 500 MCM conductor was made safe at each end and secured to the back of each panel.
Since the main breaker is rated for 800 amps and dual 500 MCM conductors are rated for 760 amps (assuming 75-degree Celsius conductors were used) the interim installation is acceptable.
end