is there a geneal industry OSHA eletrical standard or code requiring a posting(signage) of required PPE for voltage next to electrical panels or breakers?
thank you
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
keithsmith said:
is there a geneal industry OSHA eletrical standard or code requiring a posting(signage) of required PPE for voltage next to electrical panels or breakers?
thank you

I think you only have to post the level of protection required, not the individual items needed. Presumably a qualifed person would know what those items are.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
As of today the only required information is that an arc flash could occur. This is in 110.16 of the NEC.

There is no requirement in the NEC, NFPA70E, or OSHA for exact labeling requirements.

However, the next edition of NFPA 70E may include some requirements.
 

zog

Senior Member
Location
Charlotte, NC
Yes, the 2008 70E will require the labels to list at least the arc flash boundary and the Ei or the minimum PPE requirements.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Does 70E require voltage rated gloves and PPE for switching circuit breakers in a panel with the cover on?
 

zog

Senior Member
Location
Charlotte, NC
Tom,

V rated gloves - no
PPE - depends on the breaker, refer to table 130.7(C)(9)(a) and 130.7(C)(10) in the 2004 NFPA 70E. You need at least long sleeve cotton shirt and pants and safety glasses.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
zog said:
PPE - depends on the breaker, refer to table 130.7(C)(9)(a) and 130.7(C)(10) in the 2004 NFPA 70E. You need at least long sleeve cotton shirt and pants and safety glasses.

According to table 130.7(C)(10) for "arc flash" HRC 2, 3, and 4 you need leather gloves as part of your PPE, for HRC 1 hand protection is AN (as needed). Of course if you are also inside the restricted approach boundary then voltage rated gloves would also be required.
 

hutch75

Member
Location
Detroit, MI
NFPA 70e

NFPA 70e

Remember when quoting NFPA 70e that OSHA in their final rule published in Feb of this year, formally referenced 70e, but referenced the 2000 edition, not the 2008 edition, so although it is a much more thorough document, it is unenforceable. Our company wrote our spec around the 2000 version.
 

zog

Senior Member
Location
Charlotte, NC
The final rule that became effective 8/13 only covers the installation section of the 70E, phase 2 will cover the SWP's, PPE, etc of the 70E , who knows when that will be released and what version it will reference. The 2004 70E is still enforceable by OSHA through the same general duty clauses as before.
 