I am at a plant that has a 1000 KVA - 240 delta service. I want to install a 480 vac VFDs but maintenance is worried the 480 is more dangerous in both a shock hazard and arc flash respect.
I would use a delta/Wye ( solid ground) 240/480 step up transformer with OCPD on the load side feeding a distribution panel.
I believe the arc flash would be reduced on the 480 because impedance of the transformer would reduce the available arc flash current and the OCPD should trip as fast with 480 as it would if it remained at 240 therefore reducing the I^2(T).
Shock hazard would remain about the same with 277 vs 240 to ground.
Am I correct in my analysis?
Ignore what our safe work practice policy requires because sometimes people don't follow policy and I want maximum safety with or without following policy.
I would use a delta/Wye ( solid ground) 240/480 step up transformer with OCPD on the load side feeding a distribution panel.
I believe the arc flash would be reduced on the 480 because impedance of the transformer would reduce the available arc flash current and the OCPD should trip as fast with 480 as it would if it remained at 240 therefore reducing the I^2(T).
Shock hazard would remain about the same with 277 vs 240 to ground.
Am I correct in my analysis?
Ignore what our safe work practice policy requires because sometimes people don't follow policy and I want maximum safety with or without following policy.