FIRERESCUE
Member
Plastic Inj. Molding Machines - anyone have experience with requirements for external 480V 3 Phase general use receptacles mounted to a machine for auxiliary equipment and fed from a remote secondary source? We have 4 receps on each machine. Each recep is 30 Amps and tapped from 60 Amp fused disconnect w/60A fuses. Each piece of auxiliary equipment has its own disconnect, overload and short circuit protection sized per machine as well as corresponding twist lock male plug. The press disconnect powers down all press power but all external auxiliary receps are still live and disconnect is not within sight. We have maintenance personnel arguing with management about no warning signs for secondary power, no shut down procedures and no auxiliary recep power disconnect within sight at the machine. As far as I can tell it is perfectly legal. The argument concerns the auxilliary equipment cords or receptacles that become damaged - operators do not understand that this power is still live even with the press disconnect in the "off" state. I know this is a training and education problem but does anyone see anything wrong by the NEC standards? I looked in the NEC and NFPA 79 Articles as well and all I can find is a reference for warnings when parts are live in a de-energized state due to secondary power sources - which is not the case here. Although I disagree with management due to operator safety concerns I can't seem to give any concrete reference that proves the maintenance teams argument is valid. All wiring was performed by a reputable licensed electrical contractor.
Thanks in advance ........