i have done it many times, but i now do not do it and don't allow my men to do it. shuting down the bus for ten minutes after hours or early in the morning cost a few dollars but the risk of lost of life or damage to equipment is usually great. the clearances where the tap fingers meet the bus are very narrow. i had to install an 800 amp-480 volt bus tap on a ite 4000 amp bus in an office building. when ordering the tap, they asked me a question about which side of the bus the neutral was on? i had to remove the access cover to find out. i asked the local ite representative if i could do this with the bus energized? "no problem" was the answer. well, as we removed the last screw on the cover plate, a screw support bracket inside the access hole fell down and hit the bus. quite an explosion occurred- tripped the ground fault - shut down the bus feeding 34 stories of offices. myself and a fellow employee had some flash burns(not serious) blisters. i called the representative and he then admitted he "really" didn't know for sure before telling me it could be done while energized. we all see crazy things in installations everyday - people rig things - manufacturers cut corners - and when you tell the customer it must be shut down for the safety of your men and to protect his equipment, they usually understand. if you have the tap switch ready, the shutdown time is ten minutes!!!!