He's asking about line and load in the same raceway.Isn't that not only allowed, but also a requirement? At least if the conduit is ferrous?
Don't separate the phases in different metallic conduits.Isn't that not only allowed, but also a requirement? At least if the conduit is ferrous?
That makes sense. I was thinking switch legs.He's asking about line and load in the same raceway.
Service disconnect? Or equipment disconnect? Transferswitch feed and return?I'm running conduit outside for the disconnect. Can I used the same conduit for return? Thanks
View attachment 2580392
If there's only one switched conductor going to the disconnect, then yes. If it's both hots of a single phase 120/240, for example, then they could go in one conduit and return in another.Isn't that not only allowed, but also a requirement? At least if the conduit is ferrous?
In the latter case, if those hots supply any L-N loads, the associated grounded conductor would also need to go in one conduit and return in the other.If there's only one switched conductor going to the disconnect, then yes. If it's both hots of a single phase 120/240, for example, then they could go in one conduit and return in another.
right it's illegal to "double pass". This was an issue years ago with rural poco meters. Guys were using the same 2" EMT to hit the meter and go back up to a service drop, like to a house or barn.If there's only one switched conductor going to the disconnect, then yes. If it's both hots of a single phase 120/240, for example, then they could go in one conduit and return in another.
That was normal for rural POCO provided meter loops. They didn’t stop that practice here until soon after I found one that the utility line down had shorted to a load side up. Pulling the meter did not remove all power. We were allowed to remove meters at that time. That farmer had been getting some free kWh for a while.right it's illegal to "double pass". This was an issue years ago with rural poco meters. Guys were using the same 2" EMT to hit the meter and go back up to a service drop, like to a house or barn.