He's asking about line and load in the same raceway.Isn't that not only allowed, but also a requirement? At least if the conduit is ferrous?
Don't separate the phases in different metallic conduits.Isn't that not only allowed, but also a requirement? At least if the conduit is ferrous?
That makes sense. I was thinking switch legs.He's asking about line and load in the same raceway.
Service disconnect? Or equipment disconnect? Transferswitch feed and return?I'm running conduit outside for the disconnect. Can I used the same conduit for return? Thanks
View attachment 2580392
If there's only one switched conductor going to the disconnect, then yes. If it's both hots of a single phase 120/240, for example, then they could go in one conduit and return in another.Isn't that not only allowed, but also a requirement? At least if the conduit is ferrous?