230.7 Other Conductors in Raceway or Cable. Conductors
other than service conductors shall not be installed in
the same service raceway or service cable.
Exception No. 1: Grounding conductors and bonding
jumpers.
Exception No. 2: Load management control conductors
having overcurrent protection.
Can a branch circuit be ran in the same pipe as the service wires that provide power to a detached residential building? Everything is from the same source of power (same service)
If this is just a feeder from the main panel, then yes you can put them in the same raceway. But if is a separate service then they have to be kept separate.
The service for the detached building comes off the meterbase on the main house, to a separate 200 amp disonnect and then to the detached building which would make it a "separate service". And therefore as iwire says, "no". Time to dig up his yard again.
??? Service wires are service wires and feeders are feeders. Service wires can not come off a "feeder breaker". Not being a nit picker but given the context of the discussion terms and definitions are important.But on a different job, I have ran other circuits within the same pipe when the service was coming off a feeder breaker on the main panel box. Reading about that in the code book I believe it mentioned if more than one circuit was ran to the same detached building, there would be a need to label the devices ran off the different circuits for identification purposes within the detached building.
[The service for the detached building comes off the meterbase on the main house, to a separate 200 amp disconnect and then to the detached building]
If it's downstream of a 200 amp disconnect, it is no longer a service. Service is ahead of the disconnect. Is the second disconnect located near the meter? Multiple disconnects (up to 6) must be "grouped" to meet Code.
The service for the detached building comes off the meterbase on the main house, to a separate 200 amp disonnect and then to the detached building which would make it a "separate service". And therefore as iwire says, "no". Time to dig up his yard again.
But on a different job, I have ran other circuits within the same pipe when the service was coming off a feeder breaker on the main panel box. Reading about that in the code book I believe it mentioned if more than one circuit was ran to the same detached building, there would be a need to label the devices ran off the different circuits for identification purposes within the detached building.