I am helping a Inspector that is studying to take he IRC electrical exam. and one of the sample question is" A 240 volt single phase three wire feeder circuit has a continuous load of 65 amps. The ambient temperature of the area in which the wires are running is 70 degrees Celsius. Which of the following insulation types and wire sizes would be acceptable to feed this branch circuit if copper-clad aluminum wire was used? A. TW 3 B. UF3 C. THHN 4 D. XHHW 4 or E. C and D"
The study guide says that the answer is E. both C and D. My question is according to the the tables in the IRC E3705.1( 2014 NEC 310.15(B)(16)) but there is no allowance for the ambient temperature table IRC E3705.2 ( 2014 NEC 310.15(B)(2)(a)).
My calculation #4 THHN or XHHW at 90c is 75 amps x adjustment at 70c ambient for 90c wire is .58 = 43.5 amps.
Am I missing something?
The study guide says that the answer is E. both C and D. My question is according to the the tables in the IRC E3705.1( 2014 NEC 310.15(B)(16)) but there is no allowance for the ambient temperature table IRC E3705.2 ( 2014 NEC 310.15(B)(2)(a)).
My calculation #4 THHN or XHHW at 90c is 75 amps x adjustment at 70c ambient for 90c wire is .58 = 43.5 amps.
Am I missing something?