Looking for advice on flexible conduit type and wire type that can handle hi heat (190-220F) and in wet location to wire a HUUM Hive mini suana. What I have found so far is extreme heat liquid-tight metal flex that is capable of handling temperatures up to 302F, but im a little stumped on the appropriate wire to use. I only need to go about 2ft to the jbox in the wall. If anyone has any experience or can help recommend a wire i would greatly appreciate it. Thanks.
 
Take a look here:

 
Why aren't 90° C conductors sufficient? What part of the wiring system is going to reach 200° C?
 
It's the fear of the unknown, what will the inspector say? He could purchase several UL standards to prove it at a cost of thousands, for a few feet of wire and high temp liquid-tite. he could ask the vendor of the likely imported product, they likely don't really know or have the proof on file either.

The wire types I gave have been used in commercial cooking equipment internal wiring, connecting directly to the elements, and inside motor terminal boxes, for my lifetime, exposed to oil and grease at temperature, and with silicone insulation, I would doubt that a few sprinkles of water or high humidity would be a problem. But it's not my place to decide. And honestly, I doubt his inspector would know the listing details either. If it was me I would elect to use steel flexible conduit and the SRML wire and sleep just fine.

THHN might be just fine as well but he is really unsure what temperature it needs to operate at for sure. We don't know what the wiring connects to, the heating elements, terminal block or a contactor. I doubt whatever it is, that the wire is rated much higher than the terminal points. If he is unsure, maybe he should ask what his inspector what he want's to see.
 
I am looking for the same thing. I think part of the question for me is, what do you run the wire in? Its has to be a wet location jacket. A flexible jacket would be best. PVC coated would melt. That sort of leaves steel pipe and compression fittings. Not ideal. Any idea on a flexible jacket to make a whip to get from the heater unit to the outer wall. The sauna I am doing is wet. As in they use a ladle to pour water on the hot rocks.
 
Looking for advice on flexible conduit type and wire type that can handle hi heat (190-220F) and in wet location to wire a HUUM Hive mini suana.
OP should tell us why a +200° C conductor is required.
That's not a sauna, that's an oven. Again, what do the instructions say?

WIRINGWITHOUTEXTBOX_1.png



-Hal
 
Last edited:
I am seeing this on page 6 of the installation manual.

ATTENTION! You shall not use a non-heat-resistant cable with PVC isolation as the power cable. The junction box must be waterproof and it must be located up to 1 ³¹/₃₂" (50 cm) from the floor.

They are talking about the conductors or cable going to L1 and L2 of the heating elements from the controller as shown in "5" above. So, I'm not seeing moisture as an issue, and a silicone type SA conductor would work fine.

I also don't think they know too much either or else they would make specific recommendations for the wiring and raceway or better yet provide a length pre-terminated since it's not something the average electrician is going to have available, know about or be able to get a small quantity of in a hurry.

They appear to be Canadian but really Estonia which explains a lot.