hockeyoligist2 said:Does that mean that when I changed my well pump to 240v it still costs me the same to operate it? Geez all that trouble for nothing!
dahualin said:The principal advantages of using higher voltages in buildings are:
1. Smaller conductors
2. Lower voltage drop
3. Fewer or smaller circuits
4. Lower I2R losses (thus, more energy efficient)
Overall, save energy, save material, save money.
David
dahualin said:The principal advantages of using higher voltages in buildings are:
1. Smaller conductors
2. Lower voltage drop
3. Fewer or smaller circuits
4. Lower I2R losses (thus, more energy efficient)
Overall, save energy, save material, save money.
David
Maybe so, maybe not. Yes, conductors can be smaller, but if the conductors are properly sized you may or may not have lower voltage drop and you may or may not have lower I2R losses. Depending on the building (and the engineer) you may or may not have fewer circuits. What you do have at 480/277Y plus 208/120Y compared to 208/120Y only is panels at two voltages (which may or may not mean more panels) and step-down transformers (which take up space and generate heat).
infinity said:But back to the OP, an AC operating at 240 volts would have only half of the percentage of voltage drop of the same AC operating at 120 volts, so I2R losses would be less with the 240 volt operation.
hmspe said:Yes, conductors can be smaller, but if the conductors are properly sized you may or may not have lower voltage drop and you may or may not have lower I2R losses. Depending on the building (and the engineer) you may or may not have fewer circuits. What you do have at 480/277Y plus 208/120Y compared to 208/120Y only is panels at two voltages (which may or may not mean more panels) and step-down transformers (which take up space and generate heat).
If you take all the factors into account, including total materials cost, total installation cost, equipment efficiency (compare the 430.250 loads for a 20HP motor at 460V and at 208V -- the 208V motor VA is less), added losses in the step-down transformer(s), and added cooling loads because of transformer heat, I think you'll find that the results will vary as to which is cheaper to install and will vary as to which is cheaper to operate. There is no "one size fits all" answer to whether 480/277Y plus 208/120Y or 208/120 only is more cost effective, either first cost or operating cost, especially for small to moderate sized buildings.
Martin