Saw POLES ( construction temporary power poles for underground)

Merry Christmas

Sjogdren1

New User
Location
71107
Occupation
Electrician
My NEW local authority member Electrical inspector has required US to drive grounding electrodes for SAW POLES. AKA construction temporary power. In my location we have used a butt ground for over 20 years due to someone driving a rod through a primary cable. Are most jurisdictions requiring ground rods on temporary saw poles?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
While a common practice in many areas, I don't think that the NEC has ever permitted a butt ground as a grounding electrode.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
My NEW local authority member Electrical inspector has required US to drive grounding electrodes for SAW POLES. AKA construction temporary power. In my location we have used a butt ground for over 20 years due to someone driving a rod through a primary cable. Are most jurisdictions requiring ground rods on temporary saw poles?
811! LOL! Should have been called anyway when digging any post hole.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
In California we have "Underground Allert" requirement before you can drive a ground rod. Isn't required in all states ?
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Here in Georgia, you were required to have a certification to move a shovel full of dirt. Blue card I think it was called. Never got carded by an inspector. I assume it’s still required.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
We have a call before you dig but I don't think driving a ground rod is part of it
 

jmellc

Senior Member
Location
Durham, NC
Occupation
Facility Maintenance Tech. Licensed Electrician
Never heard of butt grounding. We drove 1 gound rod in the 70's for a sawpole & have been doing 2 ever since it became a requirement for buildings. Someone describe butt grounding to me?
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Never heard of butt grounding. We drove 1 gound rod in the 70's for a sawpole & have been doing 2 ever since it became a requirement for buildings. Someone describe butt grounding to me?
It's when a 6' coil of wire is stapled to the butt of the pole. (Or post)

Now we use something like this:
IMG_3158.jpeg
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Looked it up, 60 cm x 60 cm, it will not meet NEC.
Where in the NEC did you look I'm guessing plates electrodes? Other listed electrodes are permitted {250.52(A)(6)} so the question is does this meet the other listed electrode requirement? It probably doesn't but I'm wonder what does meet 250.52(A)(6)?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Are butt grounds considered to be the same as Article 250 plate electrodes?
My understanding of a butt grounding electrode is just the GEC spiral wrapped around the butt of the pole.
This is from a utility pole on a 34.5kV line.
1726931227118.jpeg


I have never seen a plate installed on the bottom of the pole. If you installed a plate with 2 square feet in contact with the earth at the bottom of the pole, it would be compliant.
 