mshields
Senior Member
- Location
- Boston, MA
Actually, my question is about SSBJ's. Specifically, I'm looking at the grounding of an generator that will have associated with it, 2, 4 pole ATS's. So this is a separately derived system. As such the neutral will be bonded to ground at the generator. The generator will have a 450A MCB. Is the ground conductor from the center of the generators Y connection to this the enclosure housing the 450A breaker an Equipment Ground conductor (sized per one table) or is it an SSBJ (sized per the new table in the 250). Beyond this breaker, that's an EGC and therefore sized by 250.122.
Do I have that straight?
OR
Is it only an SSBJ if the neutral to ground bonding takes place at that first 450A main breaker?
Thanks,
Mike
Do I have that straight?
OR
Is it only an SSBJ if the neutral to ground bonding takes place at that first 450A main breaker?
Thanks,
Mike