I did a tenant finish on a core and shell. all panels provided by landlord.
I did no SC calcs.
My plans got rejected with the following comments:
"1. E.10 NEC 110.9 & 10 need point to point AIC to panel board and controllers & Hvac equipment until below 5Kaic."
"5. E3.0; NEC110.10 Verify SCCR rating is below listing." E3 is a lighting sheet.
So I have to do SC calcs to every HVAC equipment off of this panel? This is a shock to me. There are heat pumps, fan coils with electric heat, and exhaust fans on this panel.
this is new to me. None of these comments seem relevant or correct, Has the code passed me by?
/
1. E.10; NEC 110.9 & 10 need point to point AIC to panel board and controllers & Hvac equipment until below 5Kaic.
I did no SC calcs.
My plans got rejected with the following comments:
"1. E.10 NEC 110.9 & 10 need point to point AIC to panel board and controllers & Hvac equipment until below 5Kaic."
"5. E3.0; NEC110.10 Verify SCCR rating is below listing." E3 is a lighting sheet.
So I have to do SC calcs to every HVAC equipment off of this panel? This is a shock to me. There are heat pumps, fan coils with electric heat, and exhaust fans on this panel.
this is new to me. None of these comments seem relevant or correct, Has the code passed me by?
/
1. E.10; NEC 110.9 & 10 need point to point AIC to panel board and controllers & Hvac equipment until below 5Kaic.