I`m studying to take the masters. I know when you are sizing feeder protection you have to take the next size down on protection if the size is not standard. Also on overload protection you have to take the next size down if you are using fuses and the size is not standard. In Mike Holt`s 2005 NEC Exam Prep Book chapter 11 page 458 he shows an A/C unit with rated load current of 18Amp, max. fuse size on nameplate is 40amp, minimum circuit ampacity is 23 amp.
In the short circuit example part of the problem goes like this:
Protection size=18A x1.75
Protection size=31.5
Next size down. 30A [240.6(A)]
My question is I don`t find where you have to size down? I`m missing something. Can anyone help?
In the short circuit example part of the problem goes like this:
Protection size=18A x1.75
Protection size=31.5
Next size down. 30A [240.6(A)]
My question is I don`t find where you have to size down? I`m missing something. Can anyone help?