Attached is the panel board GA drawing . All the breakers have a interrupting capacity of 65kA @ 480V AC, then how come short circuit rating of the panel board is mentioned as 42kA
Probably because in their breaker line, the next lower breaker rating is 22kAIC or 25kAIC and the AFC was over that amount, but under 42kA.But why would the PB mfg sell a panelboard with a 42 SCCR and 65k breakers (assuming the FC is over 42k)?
Probably because in their breaker line, the next lower breaker rating is 22kAIC or 25kAIC and the AFC was over that amount, but under 42kA.
Still, I get your point, it seems kind of silly, especially if you have ever compared a panel built for 42kA bracing vs one with 65kA bracing. In one case I saw, it was one more mounting screw on the insulation.