But depending on the design of the VFD you may or may not have to consider motor contribution to the current upstream of the VFD. yes?You shouldn't put contactors downstream of VFDs, it's a good way to kill the VFD. What's the purpose of them? The VFD should be controlling the On-Off of the motor.
As far as an "arc flash analysis", there is not difference in how you would determine the power going in the box. The fact that the VFD changes the feed to the motors to 3 phase is irrelevant.
Only if it is an Active Front End Line Regenerative VFD used for constant braking applications. For the most part nobody makes them smaller than 10HP, but one could possibly use a 10HP AFE LR VFD for a 2HP motor if one had a penchant for wasting mass quantities of money.But depending on the design of the VFD you may or may not have to consider motor contribution to the current upstream of the VFD. yes?
Some utilities require a disconnect at the meter, it’s usually non-fused.That non-fused main looks like a violation of 230.91. There is no upstream protective device to clear an arcing fault on the incoming lugs of the 100A MCB in the control panel. You'll get a red sticker instead of an orange one. IMHO, you don't need a sticker anywhere downstream of the panel, so why try to crunch the numbers?
True, but I would expect a disconnect like that to be upstream of the meter.Some utilities require a disconnect at the meter, it’s usually non-fused.
I have never seen one ahead of the meter. Always load side. Sometimes fused, some not. Nonfused transfer switches, depending on the POCO.True, but I would expect a disconnect like that to be upstream of the meter.