bellington
- Hahira, GA
- Consultant
I have a 1107 kWh battery with 60 kW PV and a 450 kW generator. On 9/13/25, the generator was running, pushing around 200 kW into the battery, and the inverter had reported 0 amps and 0 kW for about 15 minutes. Around 7:30 pm, the inverter started reporting 6553.3 kW. The battery interpreted this as massive incoming current, and opened the contacts. Obviously, opening the circuit on the generator at 200 kW is not ideal.
Questions:
1. Does anyone know is the 65535 series of numbers is a code for an error, or fault on the Chint inverter?
2. If so, what should I check on the inverter?
Thank you,
Byron
Questions:
Thank you,
Byron