Hi all,
New person to Mike Holt forums. These questions are in regard to some confusing (at least on my part) things in sccr. I have a machine I'm retro-fitting, and it has two panels/enclosures, one is a main enclosure, the other is what I'll call a motion enclosure. The main will house a 100 amp fused disconnect, a mainline contactor, some motor starters/overload relays, and a small ethernet fieldbus coupler with I/O modules used for reading pressure switches, limit switches, etc., 460V 3Ph powers the machine. The second panel (motion), has servo drives (230V, 3Ph.) another remote bus coupler set-up, a fused disconnect 460/120v power supply, and a 30kVA 3.84%Z 460V/230V 3 Ph. drive transformer (servo) that is mounted on the outside of the panel. The drive transformer is wired to the mainline contactor, although they are approx. 30 machine feet away and reside in/on different panels. The two ethernet bus couplers I listed here, are ethernetted to two of the servo drives used in the motion cabinet. There is approx. 12kA RMS symmetrical amps fault current available to the machine where it will sit, the peak let-through current of the LPJ 100 amp fuses in the feeder (100 amp fused disconnect) will be approx. 5800 amps at that fault current. According to what I'm understanding of the calculations of sccr, the available fault current on the primary side of the drive transformer will be approx. 6500 amps, and approx. 1900 amps on the secondary side.
Here are my questions, am I correct in my statements about the primary and secondary fault currents on the servo transformer, because it looks to be saying (SB 4.3.1) with a transformer greater than 10kVA to "Use lowest sccr of secondary circuit components". Does that mean the sccr of the servo drives connected on the secondary side of that transformer are now the sccr to use for the circuit and it sidesteps the calculations that were done in my above paragraph? Also is it correct in just using the two fuses and transformer that the 460V/120V fused disconnect power supply uses in fault current calculations?
Any help would be welcomed.
New person to Mike Holt forums. These questions are in regard to some confusing (at least on my part) things in sccr. I have a machine I'm retro-fitting, and it has two panels/enclosures, one is a main enclosure, the other is what I'll call a motion enclosure. The main will house a 100 amp fused disconnect, a mainline contactor, some motor starters/overload relays, and a small ethernet fieldbus coupler with I/O modules used for reading pressure switches, limit switches, etc., 460V 3Ph powers the machine. The second panel (motion), has servo drives (230V, 3Ph.) another remote bus coupler set-up, a fused disconnect 460/120v power supply, and a 30kVA 3.84%Z 460V/230V 3 Ph. drive transformer (servo) that is mounted on the outside of the panel. The drive transformer is wired to the mainline contactor, although they are approx. 30 machine feet away and reside in/on different panels. The two ethernet bus couplers I listed here, are ethernetted to two of the servo drives used in the motion cabinet. There is approx. 12kA RMS symmetrical amps fault current available to the machine where it will sit, the peak let-through current of the LPJ 100 amp fuses in the feeder (100 amp fused disconnect) will be approx. 5800 amps at that fault current. According to what I'm understanding of the calculations of sccr, the available fault current on the primary side of the drive transformer will be approx. 6500 amps, and approx. 1900 amps on the secondary side.
Here are my questions, am I correct in my statements about the primary and secondary fault currents on the servo transformer, because it looks to be saying (SB 4.3.1) with a transformer greater than 10kVA to "Use lowest sccr of secondary circuit components". Does that mean the sccr of the servo drives connected on the secondary side of that transformer are now the sccr to use for the circuit and it sidesteps the calculations that were done in my above paragraph? Also is it correct in just using the two fuses and transformer that the 460V/120V fused disconnect power supply uses in fault current calculations?
Any help would be welcomed.