Hello,
I'm working on establishing the SCCR rating for a PLC control unit using the UL508A Supplement SB.
The available short circuit at the customer's site is unknown. Should I obtain this before proceeding or continue?
The main breaker in the control unit is a Schneider Electric HJL36080 on a line voltage of 208VAC. The SCCR for this breaker is 100kA @ 240V (per datasheet). Can this 100kA rating be used for the breaker?
The load side of the breaker goes through two contactors with an SCCR of 100kA @ 480V (per UL Certificate). Again, can this 100kA rating be used for the contactors?
Finally, the load side of the contactors goes to a Schneider Electric 9080LBA263106 distribution block. Per the UL certificate, it was tested with a JJL36250 and is rated at 65kA @ 480V. Could there be a rating for this component at 240V?
All of the loads from this block are protected by class CC (200kA @ 600V) fuses in holders rated at 200kA @ 600V.
I was hoping to have a 100kA @ 240V SCCR for the control unit. Should the value be set at 65kA @ 240V?
Thank you.
I'm working on establishing the SCCR rating for a PLC control unit using the UL508A Supplement SB.
The available short circuit at the customer's site is unknown. Should I obtain this before proceeding or continue?
The main breaker in the control unit is a Schneider Electric HJL36080 on a line voltage of 208VAC. The SCCR for this breaker is 100kA @ 240V (per datasheet). Can this 100kA rating be used for the breaker?
The load side of the breaker goes through two contactors with an SCCR of 100kA @ 480V (per UL Certificate). Again, can this 100kA rating be used for the contactors?
Finally, the load side of the contactors goes to a Schneider Electric 9080LBA263106 distribution block. Per the UL certificate, it was tested with a JJL36250 and is rated at 65kA @ 480V. Could there be a rating for this component at 240V?
All of the loads from this block are protected by class CC (200kA @ 600V) fuses in holders rated at 200kA @ 600V.
I was hoping to have a 100kA @ 240V SCCR for the control unit. Should the value be set at 65kA @ 240V?
Thank you.