I have two questions that I am unsure as to how to perform the correct SCCR calculation. I am finding it difficult to find instructions on how to perform some of these calculations for specific circumstances that I have not yet had to deal with... I am new to this, so please feel free to let me know if I am completely incorrect.
General
The machine in question is a small automation machine. It will be connected to 480vac via a bus-bar (customer to provide a fuse in the disconnect box at the bus-bar).
Question 1
The machine has a 65kA MCCB (Siemens HEG3B030L) as it's main circuit protection. This is what we connect the incoming 480 directly to. From there, a Ferraz Shawmut (mersen) power distribution block (MPDB67653) is fed. The SCCR on the PDB lists that it is 100kA if properly fused. According to the UL data, that 100kA rating can be reached when using a wide variety of fuses, however no specific circuit breakers are listed. So my question is that does the MCCB have any affect on the SCCR of the PDB. I can't see how it would, as i cannot find any data saying using these two in series will yeild any SCCR rating, however I wanted to check to see if I am missing something. Lastly, can I just spec the customer to fuse the machine at the bus-bar with say an RK1 or RK5 (listed in the UL data as increasing the SCCR of the PBD to 100kA) and then I can perform the rest of my calculations with 100kA on the PDB?
Question 2
The same machine goes from the PDB to Class CC fuses, then to a 480vac -> 24vdc power supplies (Murr 85002, 20 amp). I cannot find any SCCR data on this unit. Part of me is thinking that I don't have to include this in my SCCR calculation because this would be considered a control circuit, however I am unsure. If I can exclude this from the SCCR calcuation, does the amp output of the device make any difference (say i were to be using a 40amp instead of the 20 amp)?
Thanks for your time - I really appreciate any help and advice.
General
The machine in question is a small automation machine. It will be connected to 480vac via a bus-bar (customer to provide a fuse in the disconnect box at the bus-bar).
Question 1
The machine has a 65kA MCCB (Siemens HEG3B030L) as it's main circuit protection. This is what we connect the incoming 480 directly to. From there, a Ferraz Shawmut (mersen) power distribution block (MPDB67653) is fed. The SCCR on the PDB lists that it is 100kA if properly fused. According to the UL data, that 100kA rating can be reached when using a wide variety of fuses, however no specific circuit breakers are listed. So my question is that does the MCCB have any affect on the SCCR of the PDB. I can't see how it would, as i cannot find any data saying using these two in series will yeild any SCCR rating, however I wanted to check to see if I am missing something. Lastly, can I just spec the customer to fuse the machine at the bus-bar with say an RK1 or RK5 (listed in the UL data as increasing the SCCR of the PBD to 100kA) and then I can perform the rest of my calculations with 100kA on the PDB?
Question 2
The same machine goes from the PDB to Class CC fuses, then to a 480vac -> 24vdc power supplies (Murr 85002, 20 amp). I cannot find any SCCR data on this unit. Part of me is thinking that I don't have to include this in my SCCR calculation because this would be considered a control circuit, however I am unsure. If I can exclude this from the SCCR calcuation, does the amp output of the device make any difference (say i were to be using a 40amp instead of the 20 amp)?
Thanks for your time - I really appreciate any help and advice.