milmat1
"It Can't Do That !"
- Location
- Siler City, NC USA
- Occupation
- Controls Engineer
Typical MCC / control panel design with fused disconnect cabinet. Branch circuit OCP, to drives , motors etc. This is all good.
My confusion comes at the control transformer. I have an dry type control transformer 1KVA, Maybe a utility 120V outlet etc then a 24VDC power supply.
All the control / IO etc is 24VDC. According to the UL 508A SB4.3 flowchart the transformer does not require an SCCR rating, right? But then does this mean that anything beyond the control transformer also is excluded ?