Need help with SCCR details. As an OEM building an Industrial Control Panel, ICP with 480v 3 phase input: I don't know the available fault current. I have an AB fused disconnect switch with AJT-50 fuses. According to UL, let-thru currents would be 22kA rms and 9kA peak, based on a 100kA availability.
If everything in my system is rated at least at 9kA, can I rate the SCCR for the ICP as 100kA?
The rest of the feeder circuit contains 3 MCPs (65kA rated) and a single phase 7.5kVA xfmr with class CC fuses on pri and sec circuits: 20A pri and secondary of 120v (15A fuses) and 240v (20A fuses)
Any help?