SCCR refers to EQUIPMENT, meaning that you have multiple devices in a unit and together, there is an overall SCCR that is based on EITHER the LOWEST rated device inside, a "series listing" of devices, or at the very least, an untested / unlisted "courtesy" listing of 5kA. The problem is, 5kA is basically useless in the real world.
Breakers alone have an "Interrupt Capacity" (AIC), which would be used as PART of an SCCR if they are in an assembly. So if a breaker by itself is listed at 10kAIC, then the most an assembly using them can have is an SCCR of 10kA, unless the breaker is "Series Listed" with a Main breaker for a higher value, for example 22kAIC is common. In that case then, a panel using that SPECIFIC combination could have an SCCR of 22kA.
You say that RCCB is "listed"? As what? It makes a difference. If it is UL listed under UL489, that is a legit "circuit breaker" and would be REQUIRED to have an AIC rating as part of that listing. If not, it might be "listed" under UL1077, which is for a "supplementary protector", something different from a circuit breaker, which is then REQUIRED to be used DOWNSTREAM of another listed protective device, either a UL489 listed breaker, or a fuse that is UL listed as BRANCH protection (not all of them are). So if their documentation says it is required to have gL fuses ahead of it, that would NOT be a legitimate listing for use in North America, because gL fuses are NOT listed for Branch protection here.
But I think you are still missing something here; "10mA SCCR" would be WORSE than having NO SCCR... 10mA is likely the RCD trip level, which has nothing to do with the IC rating.