Glad to be a new member here. I have one taxing question. We are scratching our heads on WHY we can't use the feeder peek let through current of current limiting fuses to adjust the rating of BRANCH OCPDs the way you can the components.
We all have our "theories" here but we're looking for the U.L. reason for this? It does seem if your fuse limits the max current from the feeder to 6kA, then a 10kA branch breaker would be safe up for the rating of the feeder fuse.
So, why? And thanks in advance. These forums are a wealth of information on all the things you don't learn in college.