A customer has purchased a 75 HP packaged (skidded with enclosure) air compressor with integral control panel which includes 480 VAC dist. block, 75 HP VFD, control transformer (fused) and small ATL starter (fused). The panel has a sticker with SCCR of 10 kA. Available fault current exceeds that.
I am having trouble coordinating with compressor supplier to confirm what is the limiting component in the panel (I believe it is the distribution block as the drive appears be rated up to 100KA depending on fusing), and what can be done to eliminate it. I did not note any UL or other NRTL sticker on the enclosure.
I am considering recommending to the customer they replace the distribution block with one listed for the available current (bussmann pdb style) and installing applicable upstream fuses, assuming I will not get a solution from the manufacturer.
I could also tell them to increase their conductor lengths by around 150' to reduce the fault current, but that does not look like a practical solution.
Any other suggestions or cautions regarding changes to the vendor panel? As it is skidded equipment, I don't know if article 409 even applies, or if UL 508 would apply.