I have a piece of lab equipment that employs hermetic compressor and nichrome heaters. I have a mains circuit of 480V that is separated from a control circuit of 115VAC by a general purpose transformer. The equipment is marked as having a 5KA SCCR.
I would like to add a small outlet to this equipment to plug in a 24VDC piece of equipment. The SCCR of the outlet is 2KA. I am using circuit breakers for the primary and secondary transformer protection, so the let through current is probably higher than 2KA. Would I have to install a current limiting fuse in line with the outlet in order to increase the SCCR of the outlet to keep the 5KA SCCR of the entire equipment?
Also, since this equipment has a main fuse requirement of 25A, and employs Hermetic Compressors, I am not even sure that it is required to be marked with an SCCR according to NEC 440.
I would like to add a small outlet to this equipment to plug in a 24VDC piece of equipment. The SCCR of the outlet is 2KA. I am using circuit breakers for the primary and secondary transformer protection, so the let through current is probably higher than 2KA. Would I have to install a current limiting fuse in line with the outlet in order to increase the SCCR of the outlet to keep the 5KA SCCR of the entire equipment?