This area in electrical code appears to be unknown by a lot of electricians. I have seen that distribution transformers may be as large as 500 kVA. The the case that there is a 500 kVA distribution transformer feeding over 100 homes, with a short impedance of 6%, is there any concern that the available fault current from the 500 kVA transformer exceeds the branch circuit breakers SCCR rating in each of the 100 homes?
Available Fault Current = 500,000 VA / ( 3^(1/3) * 240V * 0.06) = 20.05 kA
Typical house circuit breaker (15A to 30A) SCCR is only 10 kA
In this case does there have to be a smaller distribution transformer 1:1 ratio, or have current limiting fuses just for SCCR protection, expressly for the homes closest to the 500 kVA transformer?
From what I see, the largest distribution transformer you can have power a home that only has 10 kA circuit breakers is 249 kVA (with 6% impendence).
Available Fault Current = 500,000 VA / ( 3^(1/3) * 240V * 0.06) = 20.05 kA
Typical house circuit breaker (15A to 30A) SCCR is only 10 kA
In this case does there have to be a smaller distribution transformer 1:1 ratio, or have current limiting fuses just for SCCR protection, expressly for the homes closest to the 500 kVA transformer?
From what I see, the largest distribution transformer you can have power a home that only has 10 kA circuit breakers is 249 kVA (with 6% impendence).