Schedule 80 flat roof

Status
Not open for further replies.

cybersurge

Member
Location
California
Occupation
GC
I am running single phase 220 #3 via schedule 80. Can I go over AC ducts fasting with uni to the flat roof or do I have to go under AC ducts? If under what would be the code that references that.
 
PVC on a roof is not really a great plan so I would put it in the shade as much as possible if you have to use it
 
PVC on a roof is not really a great plan so I would put it in the shade as much as possible if you have to use it
Thanks for that. Is it code to run schedule 80 on a flat roof that is always exposed to the sun. Also, is it code to run 2" schedule 80 over a AC don't if I fasten it to the roof with 18" high unistrut fastened to the roof?
 
Expansion of PVC is substantial on a rooftop. Would go with EMT or Rigid if you have the option.
 
Thanks for that. Is it code to run schedule 80 on a flat roof that is always exposed to the sun. Also, is it code to run 2" schedule 80 over a AC don't if I fasten it to the roof with 18" high unistrut fastened to the roof?
Check 352.44 for expansion rate. Suspended above a roof you will get a lot of sagging. Also 352.12(D) Ambient Temperatures. Where subject to ambient temperatures in excess of 50°C (122°F) unless listed otherwise. You could easily exceed that on a roof top. Have melted the bottoms of my boots on a roof.
 