When calculating the lighting load for a school, stage lighting,using the standard method, my understanding is that I am supposed to use 1 VA per sq.foot. where is this rule stated?
Table 220.12, under the "In any of the preceding..." section, "Assembly halls and auditoriums" therein.When calculating the lighting load for a school, stage lighting,using the standard method, my understanding is that I am supposed to use 1 VA per sq.foot. where is this rule stated?
Table 220.12, under the "In any of the preceding..." section, "Assembly halls and auditoriums" therein.
With that said, keep in mind this is the minimum for service and feeder load determination. You can use a higher amount, and you actually have to use a higher amount if a higher amount is connected.
Note it alo applies to auditoriums. Doesn't say stage specifically... just an assumption I believe most would make. Generally a stage is part of an assembly area such as an auditorium in a school.Why does stage lighting fall under assembly halls?