Can anyone help me with the following? I have several SCR controlled heaters on a three phase, 3 wire 480VAC system, ungrounded. They are on a casino vessel. Under generator power we keep getting ground fault indication, via the three light indicator system. When we switch to shore power, which is a solidly ground system at the transformer neutral all the fault indications clear up. I am thinking there could be a leakage current occuring in the SCR based controller that the ungrounded system configuration picks up, but the shore power system justs sees as a very low ground fault, and does not trip out. The SCR controllers only control A and C phase, with B phase constantly energized right up to the heater elements. Any ideas?