Screws in panelboards

Status
Not open for further replies.

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Is there any new requirement in the NEC that requires panelboards to have latching hasps instead of screws? (I searched NEC 408, 312, and 314 but didn't find anything about this.)

If so, would an older panelboard have to be upgraded if a new breaker were installed to run a new feeder?

I have a client that asked about this although I've never heard of it.

Steve
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Re: Screws in panelboards

Thanks for the replies. 110.3 (B):

"Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling."

Not quite what I expected, but it does make me wonder if my client ment the panelboard once had hasps that they lost or broke and then replaced with screws.
 