Let's beat this dead horse. This is a pick your battles issue, but because the inspector walked off I am asking.
Today, my inspector walked off the job and wrote a correction for 2x4 fixtures not having 4 screws.
On several OSHPD jobs I have had structural details that show:
10# or less (1) 12 gage ceiling wire
10# to 56# (2) 12 gage ceiling wires and 2 screws at opposite corners
more than 56# (4 minimum) 12 gage ceiling wires and more 4 minimum screws.
I mentioned this to the inspector, but said I will get my apprentice to fix it. The inspector said call me when you fix it and left, and would not inspect the rest of the rooms.
Please, what is the definitive answer? There has to be a code. A UBC or CBC or seismic. This is one of those areas where inspectors push contractors around, like with gas bond or eccentric knockouts.
Today, my inspector walked off the job and wrote a correction for 2x4 fixtures not having 4 screws.
On several OSHPD jobs I have had structural details that show:
10# or less (1) 12 gage ceiling wire
10# to 56# (2) 12 gage ceiling wires and 2 screws at opposite corners
more than 56# (4 minimum) 12 gage ceiling wires and more 4 minimum screws.
I mentioned this to the inspector, but said I will get my apprentice to fix it. The inspector said call me when you fix it and left, and would not inspect the rest of the rooms.
Please, what is the definitive answer? There has to be a code. A UBC or CBC or seismic. This is one of those areas where inspectors push contractors around, like with gas bond or eccentric knockouts.