T tonype Senior Member Location New Jersey Apr 23, 2023 #1 In progress addition to a home. I noticed SD/SEC tucked under the wood framed rake extension - concerned about fire and damage (abrasion to the conductor insulation). Is there some reference standard/guideline on this? Attachments DSCF8235 (2).JPG 222.4 KB · Views: 42
In progress addition to a home. I noticed SD/SEC tucked under the wood framed rake extension - concerned about fire and damage (abrasion to the conductor insulation). Is there some reference standard/guideline on this?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Apr 23, 2023 #2 Concern is warranted... 230.9 & 230.24