is main service disconnect , the same as the first disconnect?
the reason for this question is, there is a sds feeding 2 panels,
panel 1 is within sight of the xfmr 75kva 480/208/120 wye 3 ph
panel 2 is 120' away, the first disconnect for panel 2 is fused within sight of the xfmr , the egc and neutral pass thru onto the main panel which is 120' away which is a 100amp 3 ph panel with main.
so the bonding bar, strap or wire or screw would be used here, correct?
if so wouldn't there be a parallel path back the 120' to the xfmr?