Is this possible? Here was my thought process when I was just reading through some old posts for fun gaining knowledge. One post read about sizing generator conductors.
Let's say single phase gen SDS (neutral of gen connected to ground run 4-wire)
All NEC 05
445.13 It shall be permitted to size the neutral conductors in accordance with 220.61.
220.61 The feeder or service neutral load shall be the maximum unbalance of the load determined bythis article (in this theoretical case lets assume 99% of loads are 2 phase 240 loads no neutral...very low low unbalanced load)
now of SDS systems 250.30 (A) (2)says
Let's say single phase gen SDS (neutral of gen connected to ground run 4-wire)
All NEC 05
445.13 It shall be permitted to size the neutral conductors in accordance with 220.61.
220.61 The feeder or service neutral load shall be the maximum unbalance of the load determined bythis article (in this theoretical case lets assume 99% of loads are 2 phase 240 loads no neutral...very low low unbalanced load)
now of SDS systems 250.30 (A) (2)says
Equipment Bonding Jumper Size
Where a bonding jumper of the wire type is run with the derived phase conductors from the source of a separately derived system to the first disconnecting means, it shall be sized in accordance with 250.102(C), based on the size of the derived phase conductors.
It seems to me that this Equipment bonding jumper is going to have to be a lot larger than the ungrounded conductor.
Does anyone see anything wrong with this thinking?
It seems to me that this Equipment bonding jumper is going to have to be a lot larger than the ungrounded conductor.
Does anyone see anything wrong with this thinking?