My name is Charlie Browning. I'm an electrical engineer with Black & Veatch in Charlotte, NC (please don't hold the EE against me ).
I have a very interesting situation with a waste water treatment plant. We have three utility services, three generators, and five pieces of power distribution switchgear. All loads are 480-volt. We have no 277-volt loads and we have not installed any neutrals in any of the building feeders, only equipment grounds.
Per my design, the contractor has bonded the generator neutrals at the first overcurrent device. We then installed 3 phase conductors and an equipment ground from the generator switchgear to each of the utility service switchgear. Each utility service switchgear has a service entrance rated circuit breaker and the utility neutral is bonded at this location. Transfer between utility and generator is accomplished via circuit breakers for two of the utility services (Russelectric switchgear automatic transfer scheme) and via a 3-pole automatic transfer switch at one of the switchgear. I can e-mail you the jpeg or ACAD drawing file if it will help explain the situation.
The electrical inspector is telling us that we must install 5 conductors (3 phase, 1 grounded [neutral], and 1 equipment ground) from the generator switchgear to each of the utility service switchgears. He does not accept my explanation/reasoning that we are treating the generators as SDSs and bonding at the first overcurrent device. He is saying that the generator and utility neutrals are connected together via the equipment grounds (which is true, they are connected via the main bonding jumper at each of the utility service switchgears).
If you're willing to help, my e-mail address is browningcw@bv.com My phone number is 704-510-8416.
Again, I can send you a JPG or ACAD 2000 drawing file to help explain. Or I can fax a drawing to you and call you to discuss.
Thanks in advance for your assistance and time.
Charlie Browning
Black & Veatch
I have a very interesting situation with a waste water treatment plant. We have three utility services, three generators, and five pieces of power distribution switchgear. All loads are 480-volt. We have no 277-volt loads and we have not installed any neutrals in any of the building feeders, only equipment grounds.
Per my design, the contractor has bonded the generator neutrals at the first overcurrent device. We then installed 3 phase conductors and an equipment ground from the generator switchgear to each of the utility service switchgear. Each utility service switchgear has a service entrance rated circuit breaker and the utility neutral is bonded at this location. Transfer between utility and generator is accomplished via circuit breakers for two of the utility services (Russelectric switchgear automatic transfer scheme) and via a 3-pole automatic transfer switch at one of the switchgear. I can e-mail you the jpeg or ACAD drawing file if it will help explain the situation.
The electrical inspector is telling us that we must install 5 conductors (3 phase, 1 grounded [neutral], and 1 equipment ground) from the generator switchgear to each of the utility service switchgears. He does not accept my explanation/reasoning that we are treating the generators as SDSs and bonding at the first overcurrent device. He is saying that the generator and utility neutrals are connected together via the equipment grounds (which is true, they are connected via the main bonding jumper at each of the utility service switchgears).
If you're willing to help, my e-mail address is browningcw@bv.com My phone number is 704-510-8416.
Again, I can send you a JPG or ACAD 2000 drawing file to help explain. Or I can fax a drawing to you and call you to discuss.
Thanks in advance for your assistance and time.