At work I have discovered 2 gen. sets that were installed in 04 under the 2002 code at communication sites. The gen.sets were installed as SDS using a three pole ATS. The installers picked up on the underground single point grounding ring. They cad welded to the ring and bonded to gen. frame and then bonded the neutral on a bonding bar. From the gen. set, which has a breaker, they ran 2 ungrounded cond. and the grounded conductor to the gen. disco on the building. They once again picked up on the underground ring and ran the grounding conductor,through separate conduit, to the disco where they again bonded the neutral.
I know that bonding to neutral in two places was wrong but what about not running a EGC with the phase conductors. Boss said the sites were thoroughly inspected at the time and were compliant. My thought is the gen. has the first OCP an EGC should have been ran to the disconnect on the building and not the way they did it.
I know that bonding to neutral in two places was wrong but what about not running a EGC with the phase conductors. Boss said the sites were thoroughly inspected at the time and were compliant. My thought is the gen. has the first OCP an EGC should have been ran to the disconnect on the building and not the way they did it.