ceb58
Senior Member
- Location
- Raeford, NC
The AHJ over what we do installing generators at communication sites are now wanting to see nothing but switched neutrials. This would make the gen. a separately derived system. Two questions
Can any one see any benefit from switching the neutrials in these cases? I cannot. They say it is for safety of the utility side as to not induce voltage on the utility during an outage. From what little I know if there is an outage and the gen. is running the return voltage will seek it source ( the gen) and flow very little or nothing on the utility.
The other thought. You have the main service disconnect, the neutral and the GEC are bonded. The phase conductors, neutral and an EGC go to the ATS. The neutral lands on the utility side of the pole it the switch. The EGC is bonded to the housing. Now the neutral and GEC are bonded in the generator, phase conductors, neutral and EGC come into the gen. disconnect. neutrals are isolated from can and EGC is bonded to can. From there they go into ATS. Neutral lands on E side of pole, EGC bonded to can. Now would the bond of these EGC in essence still tie the neutrals together through the housing? And if you were to have a line to ground fault on the gen. side you could,for a mill-sec., induce voltage on the utility side?
Can any one see any benefit from switching the neutrials in these cases? I cannot. They say it is for safety of the utility side as to not induce voltage on the utility during an outage. From what little I know if there is an outage and the gen. is running the return voltage will seek it source ( the gen) and flow very little or nothing on the utility.
The other thought. You have the main service disconnect, the neutral and the GEC are bonded. The phase conductors, neutral and an EGC go to the ATS. The neutral lands on the utility side of the pole it the switch. The EGC is bonded to the housing. Now the neutral and GEC are bonded in the generator, phase conductors, neutral and EGC come into the gen. disconnect. neutrals are isolated from can and EGC is bonded to can. From there they go into ATS. Neutral lands on E side of pole, EGC bonded to can. Now would the bond of these EGC in essence still tie the neutrals together through the housing? And if you were to have a line to ground fault on the gen. side you could,for a mill-sec., induce voltage on the utility side?