chris kennedy
Senior Member
- Location
- Miami Fla.
- Occupation
- 60 yr old tool twisting electrician
Is there a problem with this definition?
I have a transformer, 480 delta primary and 208y/120 secondary. I'm reverse wiring this as a step up. My now 208y/120 primary EGC is bonded to the transformer enclosure. My B phase of the 480 now delta secondary is bonded to the transformer enclosure. Would this not be a direct electrical connection of the different systems grounded conductor?Separately Derived System. A premises wiring system whose power is derived from a source of electric energy or equipment other than a service. Such systems have no direct electrical connection, including a solidly connected grounded circuit conductor, to supply conductors originating in another system.